What is the minimum width of the working space in front of a 200 ampere panelboard that is 20 in wide?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 7064
- D: 30 in
Explanation
Section 110.26(A)(2) requires the working space to be at least 30 in wide or the width of the equipment, whichever is greater. A 20 in panel still needs 30 in.