When sizing motor branch-circuit conductors and short-circuit protection for a general-purpose motor, which current must be used?

Exactly one answer is correct.

Show solution

Correct answer to question 8003

  • A: The full-load current from the NEC motor tables

Explanation

Section 430.6(A)(1) requires the table values (Tables 430.247 to 430.250) rather than the nameplate current for conductor ampacity and for short-circuit and ground-fault protection. The table values give a consistent, conservative basis.