A motor with a service factor of 1.0 has a nameplate current of 20 A. What is the maximum separate overload setting under 430.32(A)(1)?

Exactly one answer is correct.

Show solution

Correct answer to question 8008

  • A: 23 A

Explanation

With a service factor of 1.0, the overload may not exceed 115 percent of nameplate current. 20 A times 1.15 equals 23 A. 25 A would apply only to motors with a 1.15 service factor.