What is the maximum rating of a dual-element time-delay fuse used as motor branch-circuit short-circuit and ground-fault protection?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 8012
- B: 175 percent of full-load current
Explanation
Table 430.52 allows dual-element (time-delay) fuses up to 175 percent of the table full-load current for common ac motors. Their time delay carries starting current, so a lower percentage is needed than for nontime delay fuses.
More questions: Motors, HVAC, Generators and Transformers
- 8013What is the maximum rating of a nontime delay fuse used for motor branch-circuit short-circuit and ground-fault protection?
- 8014What is the maximum setting of an instantaneous trip breaker for a squirrel cage motor other than Design B energy efficient?
- 8015The calculated motor short-circuit protection value does not match a standard size. What does 430.52 permit?
- 8016A three-phase motor has a table full-load current of 40 A. What is the maximum inverse time breaker rating for its branch circuit, without using exceptions?
- 8017A motor has a table full-load current of 22 A. Dual-element fuses are used for branch-circuit short-circuit protection. What is the maximum standard fuse size, applying the next higher size rule?