Question 8016 of 749 · Maryland Journeyperson Electrician Exam
A three-phase motor has a table full-load current of 40 A. What is the maximum inverse time breaker rating for its branch circuit, without using exceptions?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 8016
- A: 100 A
Explanation
Table 430.52 permits 250 percent for an inverse time breaker. 40 A times 2.5 equals 100 A, which is a standard size. 50 A results from wrongly applying 125 percent.
More questions: Motors, HVAC, Generators and Transformers
- 8017A motor has a table full-load current of 22 A. Dual-element fuses are used for branch-circuit short-circuit protection. What is the maximum standard fuse size, applying the next higher size rule?
- 8020Where must a motor disconnecting means be located in relation to the motor and driven machinery?
- 8021What does the NEC mean when it says equipment is in sight from other equipment?
- 8022What is the minimum ampere rating of a motor disconnecting means for a motor rated 1000 volts or less?
- 8023A motor disconnect switch for a 10 hp motor must be rated in which unit?
- 8024How many conductors must a motor disconnecting means open?