Question 8023 of 749 · Maryland Journeyperson Electrician Exam
A motor disconnect switch for a 10 hp motor must be rated in which unit?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 8023
- D: Horsepower
Explanation
Section 430.109(A)(1) generally requires a motor-circuit switch to be rated in horsepower. Molded case breakers and switches and other listed devices are also permitted.
More questions: Motors, HVAC, Generators and Transformers
- 8024How many conductors must a motor disconnecting means open?
- 8025What must a motor disconnecting means clearly indicate?
- 8027What is the minimum rating of a motor controller?
- 8028Where must the disconnecting means for a motor control circuit be arranged?
- 8032What does the code letter on a motor nameplate indicate?
- 8034Feeder conductors supplying several motors must have an ampacity of at least what?