Question 8034 of 749 · Maryland Journeyperson Electrician Exam

Feeder conductors supplying several motors must have an ampacity of at least what?

Exactly one answer is correct.

Show solution

Correct answer to question 8034

  • D: 125 percent of the largest motor FLC plus the sum of the FLCs of the other motors

Explanation

Section 430.24 requires 125 percent of the full-load current of the highest rated motor plus the sum of the full-load currents of the other motors. Other loads are added as their own rules require.