A feeder supplies three motors with table FLCs of 40 A, 20 A and 10 A. What is the minimum feeder conductor ampacity?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 8035
- A: 80 A
Explanation
Section 430.24 applies 125 percent to the largest motor only. 40 A times 1.25 equals 50 A, plus 20 A plus 10 A gives 80 A. 87.5 A would wrongly apply 125 percent to all motors.