What is the minimum rating of a motor controller?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 8027
- B: A horsepower rating not lower than that of the motor
Explanation
Section 430.83(A) requires controllers to have a horsepower rating at the application voltage not lower than the horsepower rating of the motor, with listed exceptions. The controller must handle the motor's starting and running currents.
More questions: Motors, HVAC, Generators and Transformers
- 8028Where must the disconnecting means for a motor control circuit be arranged?
- 8032What does the code letter on a motor nameplate indicate?
- 8034Feeder conductors supplying several motors must have an ampacity of at least what?
- 8035A feeder supplies three motors with table FLCs of 40 A, 20 A and 10 A. What is the minimum feeder conductor ampacity?
- 8036How is the maximum feeder short-circuit and ground-fault protective device for a motor feeder determined?
- 8037The largest motor on a feeder has a 100 A branch-circuit breaker. The other motors have FLCs of 20 A and 10 A. What is the maximum standard feeder breaker size?