How many overload units are required for a three-phase ac motor?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 8010
- B: Three, one in each phase
Explanation
Table 430.37 requires three overload units for three-phase ac motors, one in each phase conductor. This protects the motor even if one phase is lost.
More questions: Motors, HVAC, Generators and Transformers
- 8011What is the maximum rating of an inverse time breaker used as motor branch-circuit short-circuit and ground-fault protection for a standard squirrel cage motor?
- 8012What is the maximum rating of a dual-element time-delay fuse used as motor branch-circuit short-circuit and ground-fault protection?
- 8013What is the maximum rating of a nontime delay fuse used for motor branch-circuit short-circuit and ground-fault protection?
- 8014What is the maximum setting of an instantaneous trip breaker for a squirrel cage motor other than Design B energy efficient?
- 8015The calculated motor short-circuit protection value does not match a standard size. What does 430.52 permit?