Question 8058 of 749 · Maryland Journeyperson Electrician Exam
Within how many seconds must a legally required standby system provide power after loss of normal supply?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 8058
- C: 60 seconds
Explanation
Section 701.12 requires legally required standby systems to have power available within the time needed for the application, but not more than 60 seconds. This is longer than the 10 second limit for emergency systems.