Question 8070 of 938 · Maryland Journeyperson Electrician Exam
Under what condition may a dry-type transformer be installed above a suspended ceiling?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 8070
- D: If it is 1000 volts or less, 50 kVA or less, and the space is not permanently closed in
Explanation
Section 450.13(B) allows dry-type transformers of 1000 volts or less and not over 50 kVA in hollow spaces of buildings, such as above suspended ceilings, when the space is not permanently closed in by structure. Ventilation and separation rules still apply.
More questions: Motors, HVAC, Generators and Transformers
- 8071A transformer is located out of sight of its supply disconnect. What does 450.14 require?
- 8072Oil-insulated transformers installed indoors are generally required to be installed in what?
- 8073What is the general fire resistance rating required for transformer vault walls and roofs?
- 8074Secondary conductors leave a transformer and do not exceed 10 ft in length. What may they terminate in without protection at the secondary terminals?
- 8075Capacitors rated 1000 volts or less must discharge their residual voltage to what level within what time after disconnection?
- 8076What is the minimum ampacity of conductors supplying a capacitor?