Question 8074 of 749 · Maryland Journeyperson Electrician Exam
Secondary conductors leave a transformer and do not exceed 10 ft in length. What may they terminate in without protection at the secondary terminals?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 8074
- A: A single circuit breaker or set of fuses that limits the load to the conductor ampacity
Explanation
Section 240.21(C)(2) permits secondary conductors up to 10 ft long without overcurrent protection at the transformer if they meet the ampacity conditions and terminate in a single circuit breaker or set of fuses that limits the load to their ampacity.
More questions: Motors, HVAC, Generators and Transformers
- 8075Capacitors rated 1000 volts or less must discharge their residual voltage to what level within what time after disconnection?
- 8076What is the minimum ampacity of conductors supplying a capacitor?
- 8078Why are capacitors installed in motor circuits in industrial plants?
- 8001Branch-circuit conductors supplying a single continuous-duty motor must have an ampacity of at least what percentage of the motor full-load current?
- 8002A continuous-duty motor has a table full-load current of 28 A. What is the minimum ampacity of its branch-circuit conductors?
- 8003When sizing motor branch-circuit conductors and short-circuit protection for a general-purpose motor, which current must be used?