Why are capacitors installed in motor circuits in industrial plants?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 8078
- B: To improve the lagging power factor caused by inductive loads
Explanation
Induction motors draw lagging reactive current. Capacitors supply leading reactive current, which raises the power factor and lowers the line current for the same real power. Article 460 covers their installation.