A patient care space in which failure of equipment is likely to cause only minor injury to patients or caregivers is classified as which category?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 9030
- C: Category 2
Explanation
Category 2 is the general care space, such as inpatient bedrooms and examination rooms where failure could lead to minor injury. Category 1 is critical care, while Category 3 and Category 4 are basic care and support spaces.