Question 9031 of 749 · Maryland Journeyperson Electrician Exam
Branch circuits serving patient care spaces must provide two equipment grounding paths. Which combination meets this requirement?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 9031
- C: A metal raceway or cable armor qualifying as an EGC plus an insulated copper equipment grounding conductor
Explanation
Wiring in patient care spaces must use a metal raceway or cable with a metal armor or sheath that qualifies as an equipment grounding conductor, and it must also contain an insulated copper equipment grounding conductor. This redundancy reduces shock risk to patients.
More questions: Special Occupancies
- 9035The essential electrical system of a hospital is divided into which branches?
- 9036Article 518 for assembly occupancies applies to buildings or portions of buildings designed for the gathering of how many persons or more?
- 9038At a carnival, overhead conductors must maintain what minimum horizontal clearance from amusement rides and attractions?
- 9039At a carnival, circus, or fair, 125-volt, single-phase, 15- and 20-ampere receptacles used by personnel or readily accessible to the public require what protection?
- 9047Every RV site with an electrical supply in an RV park must be equipped with at least which receptacle?