Question 9033 of 871 · Maryland Journeyperson Electrician Exam
Each patient bed location in a Category 2 (general care) space must be provided with at least how many receptacles?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 9033
- D: 8
Explanation
General care patient bed locations require a minimum of eight receptacles, which must be hospital grade or listed for the purpose. Critical care bed locations require more, at least 14.
More questions: Special Occupancies
- 9034Each patient bed location in a Category 1 (critical care) space must be provided with at least how many receptacles?
- 9035The essential electrical system of a hospital is divided into which branches?
- 9036Article 518 for assembly occupancies applies to buildings or portions of buildings designed for the gathering of how many persons or more?
- 9038At a carnival, overhead conductors must maintain what minimum horizontal clearance from amusement rides and attractions?
- 9039At a carnival, circus, or fair, 125-volt, single-phase, 15- and 20-ampere receptacles used by personnel or readily accessible to the public require what protection?
- 9040A ride at a carnival requires a disconnecting means. Where must it be located?