Each patient bed location in a Category 1 (critical care) space must be provided with at least how many receptacles?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 9034
- A: 14
Explanation
Critical care patient bed locations require at least 14 receptacles, with at least one connected to the normal system branch circuit or to a critical branch circuit supplied by a different transfer switch. General care bed locations need at least eight.