Question 9046 of 871 · Maryland Journeyperson Electrician Exam
When a mobile home is supplied by a listed power supply cord, what is the cord rating?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 9046
- D: 50 amperes
Explanation
A mobile home power supply cord, where used, is a single listed cord rated 50 amperes with four conductors including an equipment grounding conductor. Larger loads require a permanently installed feeder instead.