What is the minimum clearance over a pool water surface for an insulated overhead service drop of 0 to 750 volts supported on a messenger with a grounded neutral?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 10019
- B: 22.5 ft
Explanation
The table of overhead conductor clearances over pools gives 22.5 ft above the water surface or base of the diving platform for insulated cables of 0 to 750 volts supported on a solidly grounded bare messenger or neutral. Other conductor types, such as bare open conductors, need greater clearance.