Question 10033 of 749 · Maryland Journeyperson Electrician Exam
A commercial spa requires an emergency shutoff for the recirculation and jet system. Where must it be installed?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 10033
- D: Readily accessible, clearly labeled, within sight of the spa, and at least 5 ft away from it
Explanation
A clearly labeled emergency shutoff or control switch must be installed at least 5 ft away from, adjacent to, and within sight of the spa or hot tub, and must be readily accessible. Single-family dwellings are exempt.
More questions: Special Equipment, Pools, PV and EV
- 10036How must a hydromassage bathtub be supplied?
- 10038For a fountain, which equipment requires GFCI protection unless it is listed for operation at low voltage?
- 10042A pool pump motor is connected to a single-phase, 240-volt, 20-ampere branch circuit. What protection is required for the outlet?
- 10044What is the maximum PV system voltage permitted for PV systems on one- and two-family dwellings?
- 10045What is the maximum PV system voltage on or in buildings other than one- and two-family dwellings?
- 10046A PV module has a short-circuit current (Isc) of 10 amperes. Using the standard method, what is the maximum circuit current for that PV circuit?