For most Class 2 power sources, what is the maximum nameplate output?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 11022
- A: 100 VA
Explanation
Class 2 power sources are generally limited to 100 VA output, as set by the limits in Chapter 9 Tables 11(A) and 11(B). Higher outputs fall outside Class 2.