Five 5 kW household dryers are supplied by one feeder. What is the calculated dryer load under the NEC 2020/2023?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 12030
- B: 21,250 VA
Explanation
Five dryers at 5,000 VA each give 25,000 VA (220.54 and Table 220.54). The demand factor for five dryers is 85 % in the NEC 2020/2023, so 25,000 x 0.85 = 21,250 VA.