Question 12031 of 871 · Maryland Journeyperson Electrician Exam
Under the NEC 2020/2023, what is the demand factor for 20 household electric dryers on one feeder?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 12031
- C: 38 %
Explanation
For 12 to 23 dryers the factor is 47 % minus 1 % for each dryer above 11 (220.54 and Table 220.54). 20 dryers are 9 above 11, so 47 - 9 = 38 %.
More questions: Load Calculations
- 12032A dwelling has one electric dryer rated 3,800 W. What load must be used for it in the NEC 2020/2023 service calculation?
- 12079Under the NEC 2020 or 2023, what is the feeder load for 3 household electric dryers rated 5,000 W each?
- 12080Under the NEC 2020 or 2023, what is the feeder load for 6 household electric dryers rated 6,000 W each?
- 12081Under the NEC 2020 or 2023, what is the feeder load for 7 household electric dryers rated 5,000 W each?
- 12083Six 12 kW ranges are on one apartment feeder. What range demand load applies under the NEC 2020 or 2023?
- 12084Using NEC 2020/2023 Table 220.55 Column C, what is the demand for twelve 12 kW ranges?