Question 12083 of 871 · Maryland Journeyperson Electrician Exam
Six 12 kW ranges are on one apartment feeder. What range demand load applies under the NEC 2020 or 2023?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 12083
- C: 21 kW
Explanation
Table 220.55 Column C lists 21 kW for six ranges of not over 12 kW.
More questions: Load Calculations
- 12084Using NEC 2020/2023 Table 220.55 Column C, what is the demand for twelve 12 kW ranges?
- 12085A 28-unit building has one 12 kW range per unit. What is the range demand load under the NEC 2020 or 2023?
- 12086Under the NEC 2020 or 2023, what is the demand load for one 15 kW household range?
- 12087Under the NEC 2020 or 2023, an 8 kW cooktop and a 4 kW wall oven in the same kitchen are on one branch circuit. What is the branch circuit load?
- 12089A dwelling feeder includes a 6.4 kW range demand. What neutral load is assigned to it under the NEC 2020 or 2023?
- 12090A 120/240 V service has a maximum unbalanced load of 280 A. What neutral load is used under the NEC 2020 or 2023?