What is the allowable ampacity of 6 AWG THHN copper (90 °C column) with three current-carrying conductors in a raceway at an ambient temperature of 40 °C?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 13046
- B: 68.3 A
Explanation
Table 310.16 gives 75 A for 6 AWG copper in the 90 °C column, and the 30 °C based correction factor for 36 to 40 °C in that column is 0.91: 75 x 0.91 = 68.3 A. Using the 75 °C value with its 0.88 factor (65 x 0.88) gives 57.2 A.
More questions: Electrical Calculations
- 13047Six current-carrying 10 AWG THHN copper conductors share one raceway at 30 °C ambient. What is the adjusted ampacity from the 90 °C column?
- 13048Nine current-carrying 12 AWG THHN copper conductors are installed in one conduit at 30 °C ambient. What is the adjusted ampacity of each conductor based on the 90 °C column?
- 13049Eight current-carrying 12 AWG THHN copper conductors run through an area with a 45 °C ambient. What is the allowable ampacity using the 90 °C column?
- 13050What is the ampacity of 4 AWG THWN copper (75 °C insulation) with three current-carrying conductors at an ambient of 45 °C?
- 13051Four current-carrying 3/0 AWG THWN-2 copper conductors are installed in a raceway where the ambient is 50 °C. What is the derated ampacity from the 90 °C column?
- 13052Six current-carrying 8 AWG THHN copper conductors are in one raceway at 30 °C ambient, and all terminations are rated 75 °C. What is the maximum ampacity that may be used for each conductor?