What is the full-load current from Table 430.250 for a 10 hp, 208 volt, three-phase induction motor, and the resulting minimum conductor ampacity?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 13085
- A: 30.8 A; 38.5 A
Explanation
The 208 V column lists 30.8 A for 10 hp, and 30.8 x 1.25 = 38.5 A. 28 A is the 230 V value and 32.2 A is the 200 V value.
More questions: Electrical Calculations
- 13086A 20 hp, 460 volt, three-phase motor has a nameplate current of 26 A. Table 430.250 lists 27 A. What is the minimum branch-circuit conductor ampacity?
- 13087A 15 hp, 460 volt, three-phase squirrel-cage motor (not Design B energy efficient) has a table full-load current of 21 A. Using an inverse time breaker at its maximum percentage and the next-higher-size allowance, what breaker may be used?
- 13088A 10 hp, 230 volt, three-phase motor has a table full-load current of 28 A. What is the maximum dual-element time-delay fuse size under the basic percentage of 430.52?