What is the maximum setting, under the basic table percentage, of an instantaneous trip breaker for a 10 hp, 460 volt, three-phase squirrel-cage motor with a table full-load current of 14 A?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 13090
- B: 112 A
Explanation
Instantaneous trip breakers are limited to 800 % of full-load current for these motors: 14 x 8 = 112 A. 182 A would be 1,300 %, which needs an exception, and 35 A is the 250 % inverse time value.
More questions: Electrical Calculations
- 13091A motor has a nameplate full-load current of 24 A and a marked service factor of 1.15. What is the maximum rating of a separate overload device under 430.32(A)(1)?
- 13092A motor has a nameplate current of 40 A, a service factor of 1.0 and a temperature rise of 50 °C. What overload rating is required under the basic rule?
- 13093A motor with a 1.15 service factor and a nameplate current of 24 A trips its overloads during starting. What is the highest overload rating permitted under 430.32(C)?
- 13094A feeder supplies three 460 volt, three-phase motors with table full-load currents of 14 A, 21 A and 34 A. What is the minimum feeder conductor ampacity?
- 13095A 1 hp, 115 volt, single-phase motor has a table full-load current of 16 A. What minimum branch-circuit conductor ampacity is required?
- 13096A feeder supplies three 460 volt motors: 25 hp (34 A) protected by a 90 A inverse time breaker, 15 hp (21 A) and 10 hp (14 A). What is the maximum rating of the feeder overcurrent device?