Question 13086 of 749 · Maryland Journeyperson Electrician Exam

A 20 hp, 460 volt, three-phase motor has a nameplate current of 26 A. Table 430.250 lists 27 A. What is the minimum branch-circuit conductor ampacity?

Exactly one answer is correct.

Show solution

Correct answer to question 13086

  • B: 33.75 A

Explanation

Conductor sizing uses the table full-load current, not the nameplate value: 27 x 1.25 = 33.75 A. Using the nameplate gives 32.5 A, which is the most common error.

Next to question ›