A 9 kW, 480 volt, three-phase resistive heater is a continuous load. What is the minimum standard overcurrent device rating?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 13122
- B: 15 A
Explanation
Current is 9,000 / (480 x 1.732) = 10.8 A, and 10.8 x 1.25 = 13.5 A, so the next standard size is 15 A. Forgetting 1.732 gives 18.75 x 1.25 = 23.4 A and leads to 25 A.
More questions: Electrical Calculations
- 13123What is the inverse time breaker maximum for a 3 hp, 230 volt, single-phase motor (table FLC 17 A), allowing the next higher standard size?
- 13001A resistive heating element has a resistance of 15 ohms and is connected to 120 volts. What current does it draw?
- 13002A 4,800 watt resistive water heater is connected to a 240 volt single-phase circuit. What is the current?
- 13003What is the resistance of a 1,500 watt, 120 volt space heater element at its rated operating point?
- 13004A heater rated 4,000 watts at 240 volts is connected to a 208 volt supply. Assuming constant resistance, about how much power will it produce?
- 13005A current of 10 amperes flows through a conductor path with a total resistance of 0.5 ohm. How much power is lost as heat in the conductors?