Question 2034 of 749 · Maryland Journeyperson Electrician Exam
Service drop conductors at 120/240 volts pass over only the overhang of a roof to terminate at a through-the-roof service mast. What is the minimum clearance above the overhang?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2034
- D: 18 in.
Explanation
The overhang exception allows 18 in. where not more than 6 ft of conductors, 4 ft horizontally, pass over the roof overhang and terminate at a through-the-roof raceway or approved support. The voltage between conductors must not exceed 300 volts. See 230.24(A) Exception No. 3.
More questions: Services and Service Equipment
- 2036What must be done with a service GFPE system when it is first installed?
- 2037What is the minimum height of working space for service equipment rated 1000 volts or less?
- 2039Service conductors installed under a building are considered outside the building when they are covered by at least how much concrete?
- 2040How must each service disconnect be identified?
- 2041A detached building is supplied by one feeder. Where must its building disconnecting means be located?
- 2042Where may the service disconnecting means for a commercial building be installed?