Under the 10 ft feeder tap rule, field-installed tap conductors that leave the enclosure must have an ampacity of at least what fraction of the feeder OCPD rating?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3033
- A: One-tenth
Explanation
Field-installed 10 ft taps that leave the enclosure where the tap is made must have an ampacity of at least one-tenth of the rating of the OCPD protecting the feeder. See 240.21(B)(1).