In a multi-tenant building, who must have ready access to the OCPDs protecting the conductors supplying a tenant space?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3036
- B: Each occupant, for the OCPDs serving that occupancy
Explanation
Each occupant must have ready access to all OCPDs protecting the conductors supplying that occupancy, unless the building has continuous building management supervision. See 240.24(B).