May an OCPD be placed in a grounded conductor?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3039
- A: Only if it opens all conductors of the circuit simultaneously
Explanation
An OCPD may not be connected in series with a grounded conductor unless the device opens all conductors of the circuit at the same time, or for certain motor overload protection. See 240.22.