A dwelling unit lighting outlet in a crawl space that is at or below grade level is supplied by a 120-volt circuit. What does the NEC require?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4016
- A: The lighting outlet must be GFCI protected
Explanation
210.8 contains a specific rule that 120-volt lighting outlets in crawl spaces at or below grade require GFCI protection. This is one of the few cases where a lighting outlet, not just a receptacle, needs GFCI.
More questions: Branch Circuits, GFCI and AFCI