Question 4083 of 938 · Maryland Journeyperson Electrician Exam
A 40-ampere branch circuit supplies two receptacles. What receptacle rating is permitted?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4083
- B: 40 or 50 amperes
Explanation
Table 210.21(B)(3) permits 40-ampere or 50-ampere receptacles on a 40-ampere branch circuit. A 50-ampere circuit with multiple receptacles requires 50-ampere receptacles.
More questions: Branch Circuits, GFCI and AFCI
- 4084On a 20-ampere branch circuit, what is the maximum rating of a single cord-and-plug-connected utilization equipment not fastened in place?
- 4085A 20-ampere branch circuit supplies lighting units and also fastened-in-place utilization equipment. What is the maximum total rating of the fastened-in-place equipment?
- 4086Which loads are 40-ampere and 50-ampere branch circuits permitted to supply in any occupancy?
- 4087In a dwelling unit, a 30-ampere branch circuit is permitted to supply which of the following?
- 4088A branch circuit supplies a continuous load of 16 amperes and no noncontinuous load. What is the minimum conductor ampacity before any adjustment or correction?
- 4089A branch circuit supplies 24 amperes of continuous load and 6 amperes of noncontinuous load. What is the minimum standard overcurrent device rating?