Where ungrounded conductors 4 AWG or larger enter an enclosure through a raceway, what is required at the entry?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 6017
- A: An identified insulating bushing or equivalent protection
Explanation
Conductors 4 AWG and larger entering a cabinet, box, or enclosure from a raceway must be protected by an identified fitting with a smoothly rounded insulating surface. See 300.4 in NEC 2020 and 2023 (300.6 in NEC 2026).