Question 9026 of 749 · Maryland Journeyperson Electrician Exam
In a major repair garage for gasoline vehicles without the specified mechanical ventilation, how is the floor area up to 18 in above the floor classified?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 9026
- C: Class I, Division 2
Explanation
Article 511 treats the area up to 18 in above the floor of a repair garage handling Class I liquids as Class I, Division 2 unless ventilation at the specified rate is provided. Gasoline vapors are heavier than air and collect near the floor.