Four ranges on one feeder are rated 10, 12, 14 and 18 kW. Using NEC 2020/2023 Table 220.55 Note 2, what is the demand load?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 12088
- D: 18.7 kW
Explanation
Ranges under 12 kW count as 12 kW for averaging: (12 + 12 + 14 + 18) / 4 = 14 kW, which is 2 kW over 12, so and Column C for four ranges (17 kW) rises 10 %: 17 x 1.10 = 18.7 kW.
More questions: Load Calculations