Question 13077 of 749 · Maryland Journeyperson Electrician Exam

Using a 40 % fill area of 0.213 sq in for 3/4 inch EMT and an area of 0.0133 sq in for 12 AWG THHN, how many 12 AWG THHN conductors are permitted?

Exactly one answer is correct.

Show solution

Correct answer to question 13077

  • A: 16

Explanation

0.213 / 0.0133 = 16.0, so 16 conductors fit. Using the total area of 0.533 sq in instead of the 40 % area gives 40, which ignores the fill limit.