1 inch EMT has a total internal area of 0.864 sq in. What is the maximum cross-sectional area of a single conductor installed in it?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 13082
- B: 0.458 sq in
Explanation
A single conductor may occupy 53 %: 0.864 x 0.53 = 0.458 sq in. 0.346 is the 40 % value and 0.268 is the 31 % value for two conductors.