3/4 inch EMT has a 40 % fill area of 0.213 sq in and 14 AWG THHN has an area of 0.0097 sq in. How many 14 AWG THHN conductors are permitted when all conductors are the same size?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 13081
- A: 22
Explanation
0.213 / 0.0097 = 21.96. When all conductors are the same size and the decimal is 0.8 or larger, Chapter 9 Note 7 permits the next higher whole number, so 22 conductors are allowed.
More questions: Electrical Calculations
- 130821 inch EMT has a total internal area of 0.864 sq in. What is the maximum cross-sectional area of a single conductor installed in it?
- 13083A 25 hp, 460 volt, three-phase induction motor has a table full-load current of 34 A. What is the minimum ampacity of its branch-circuit conductors?
- 13084What minimum conductor ampacity is required for a 5 hp, 230 volt, single-phase motor? (Table full-load current 28 A.)
- 13085What is the full-load current from Table 430.250 for a 10 hp, 208 volt, three-phase induction motor, and the resulting minimum conductor ampacity?
- 13086A 20 hp, 460 volt, three-phase motor has a nameplate current of 26 A. Table 430.250 lists 27 A. What is the minimum branch-circuit conductor ampacity?
- 13087A 15 hp, 460 volt, three-phase squirrel-cage motor (not Design B energy efficient) has a table full-load current of 21 A. Using an inverse time breaker at its maximum percentage and the next-higher-size allowance, what breaker may be used?