Three 4 AWG THHN (0.0824 sq in each) and one 8 AWG THHN (0.0366 sq in) are to be installed in EMT. Which is the smallest trade size permitted? (40 % areas: 3/4 in 0.213, 1 in 0.346, 1-1/4 in 0.598 sq in)
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 13079
- C: 1 in
Explanation
Total area is 3 x 0.0824 + 0.0366 = 0.2838 sq in. This exceeds 0.213 sq in for 3/4 inch EMT but fits within 0.346 sq in for 1 inch EMT.