Question 3031 of 749 · Maryland Journeyperson Electrician Exam
When is a 1200 A feeder disconnect on a 480Y/277 volt system not required to have its own GFPE?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3031
- D: When GFPE is provided on the supply side of the feeder
Explanation
An exception to 215.10 removes the requirement where ground-fault protection is already provided on the supply side of the feeder and on the load side of any transformer supplying it. A continuous industrial process where a nonorderly shutdown adds hazards is also exempt.
More questions: Feeders and Overcurrent Protection
- 3032What is the length limit for outside feeder tap conductors that terminate at a single OCPD that is part of or next to the building disconnect?
- 3033Under the 10 ft feeder tap rule, field-installed tap conductors that leave the enclosure must have an ampacity of at least what fraction of the feeder OCPD rating?
- 3035A feeder supplies a continuous load of 160 A only. What is the minimum rating of the feeder OCPD, assuming standard equipment not rated for 100 percent operation?
- 3036In a multi-tenant building, who must have ready access to the OCPDs protecting the conductors supplying a tenant space?
- 3037Arc energy reduction is required where the highest continuous current trip setting of a circuit breaker is at least what value?
- 3039May an OCPD be placed in a grounded conductor?