A dwelling has a fully finished basement used as a recreation room. Do the 125-volt receptacles in this finished basement require GFCI protection?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4009
- A: Yes, basement receptacles require GFCI whether finished or not
Explanation
Since the 2020 edition, 210.8(A) lists basements without the word unfinished, so finished basements are included. Older editions covered only unfinished portions of basements.