A single 125-volt receptacle in an attached dwelling garage is dedicated to a chest freezer. Is GFCI protection required?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4010
- A: Yes, dwelling garage receptacles have no freezer exception
Explanation
210.8(A) covers garage receptacles in dwellings and does not contain an exception for appliances such as freezers or refrigerators. The old exceptions for single receptacles and dedicated appliances were removed many editions ago.