A motor is connected wye-start, delta-run. Conductors between the controller and the motor are selected at what portion of the full-load current?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 8033
- D: 58 percent of the motor full-load current
Explanation
Section 430.22(C) bases the conductors between controller and motor in a wye-start, delta-run connection on 58 percent of the motor full-load current. Each set of windings carries only part of the line current.