Under the 2020 NEC, a dwelling family room has a wet bar with a sink but no cooking provisions. A receptacle in the bar area is 8 ft from the sink. Is GFCI protection required by 210.8(A)?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4008
- A: No, it is not a kitchen and is more than 6 ft from the sink
Explanation
The 2020 NEC defines a kitchen as an area with a sink and permanent provisions for food preparation and cooking, so a wet bar without cooking is not a kitchen. The receptacle is also beyond 6 ft from the sink bowl, so 210.8(A) does not apply.
More questions: Branch Circuits, GFCI and AFCI
- 4009A dwelling has a fully finished basement used as a recreation room. Do the 125-volt receptacles in this finished basement require GFCI protection?
- 4010A single 125-volt receptacle in an attached dwelling garage is dedicated to a chest freezer. Is GFCI protection required?
- 4012Under the 2020 NEC, a detached dwelling storage shed has a wood floor framed 2 ft above grade and is not habitable. Do the 125-volt receptacles inside require GFCI protection under 210.8(A)?
- 4013Where must a GFCI device that provides the protection required by 210.8 be located?
- 4014When applying the 6 ft sink and bathtub distances in 210.8, how is the distance to a receptacle measured?
- 4015A dwelling has an indoor area that is a damp location, such as a covered utility room open to weather. Do 125-volt receptacles there require GFCI protection?