Under the 2020 NEC, a detached dwelling storage shed has a wood floor framed 2 ft above grade and is not habitable. Do the 125-volt receptacles inside require GFCI protection under 210.8(A)?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4012
- C: No, the accessory building item applies only to floors at or below grade
Explanation
In the 2020 NEC, 210.8(A) covered accessory buildings that have a floor located at or below grade level and are limited to storage or work areas. A shed with a raised floor did not meet that condition, so 210.8(A) did not require GFCI for the interior receptacles.