Correct answer to question 9020
- C: Electrical and thermal energy is limited so it cannot ignite the hazardous atmosphere
Explanation
Intrinsic safety limits the energy available under normal and fault conditions below the level needed to ignite the specific hazardous atmosphere. Containment of an explosion is the explosionproof method, and oil immersion is a separate protection technique.
More questions: Special Occupancies
- 9021At a motor fuel dispensing facility, how is the area up to 18 in above grade within 20 ft horizontally of a dispenser enclosure classified?
- 9022The emergency electrical disconnect for fuel dispensers must open which conductors of the circuits to the dispensing equipment?
- 9026In a major repair garage for gasoline vehicles without the specified mechanical ventilation, how is the floor area up to 18 in above the floor classified?
- 9029In health care facilities, a patient care space where failure of equipment or the electrical system is likely to cause major injury or death is which category?
- 9030A patient care space in which failure of equipment is likely to cause only minor injury to patients or caregivers is classified as which category?
- 9031Branch circuits serving patient care spaces must provide two equipment grounding paths. Which combination meets this requirement?